Initial Conditions Suspects
Hi everyone,
I'm performing a dynamic simulation for a large power system, and I got initial condition suspects for CMLDBLU2 models. Could someone help me understand how to resolve it, thanks.
INITIAL CONDITIONS SUSPECT:
I DSTATE(I) STATE(I) MODEL STATE BUS#-SCT X-- NAME --X BASKV ID
71628 0.97520E-02 0.73156 GGOV1 K+2 1 GEN 1 18.000 1
78978 -0.10885 2.2293 PIDGOV K+6 2 GEN 7G6 7.2000 6
79078 0.13712 0.89890 HYG3U1 K+6 3 GEN 13G4 13.200 4
96758 0.72085E-04 -0.15771E-02 CMLDBLU2 K+7 4 CHQ-230 230.00 2
96764 0.10331E-03 -0.15771E-02 CMLDBLU2 K+13 4 CHQ-230 230.00 2
140223 0.45542E-04 -0.41939E-02 CMLDBLU2 K+2 6 LOAD 2 115.00 N
140545 0.55042E-04 -0.33355E-02 CMLDBLU2 K 7 LOAD 2 115.00 1
142059 0.46939E-04 -0.36872E-02 CMLDBLU2 K+2 10 LOAD 5 115.00 N1
142464 0.46660E-04 -0.45174E-02 CMLDBLU2 K+2 11 LOAD 6 115.00 1
143623 0.51479E-04 0.10855E-02 CMLDBLU2 K 12 LOAD 7 115.00 1
Have you checked the log file for warnings on the CMLD models? These types of messages may exist: At bus 4, CMLD load bus voltage of 0.9471 pu is below 0.95 minimum. Original feeder Z of 0.2295 +j 0.2295 pu on SBASE will be reduced in an attempt to bring V up above 0.95 pu