Hi everyone,


I'm performing a dynamic simulation for a large power system, and I got initial condition suspects for CMLDBLU2 models. Could someone help me understand how to resolve it, thanks.

 INITIAL CONDITIONS SUSPECT:
     I      DSTATE(I)       STATE(I)        MODEL      STATE     BUS#-SCT X-- NAME --X BASKV  ID
  71628     0.97520E-02     0.73156         GGOV1       K+2     1           GEN 1       18.000  1
  78978     -0.10885        2.2293          PIDGOV      K+6     2     GEN 7G6     7.2000  6
  79078     0.13712         0.89890         HYG3U1      K+6     3     GEN 13G4    13.200  4
   96758    0.72085E-04     -0.15771E-02    CMLDBLU2    K+7     4     CHQ-230     230.00  2
  96764     0.10331E-03     -0.15771E-02    CMLDBLU2    K+13    4     CHQ-230     230.00  2
 140223     0.45542E-04     -0.41939E-02    CMLDBLU2    K+2     6     LOAD 2      115.00  N
 140545     0.55042E-04     -0.33355E-02    CMLDBLU2    K       7     LOAD 2      115.00  1
 142059     0.46939E-04     -0.36872E-02    CMLDBLU2    K+2     10    LOAD 5      115.00  N1
 142464     0.46660E-04     -0.45174E-02    CMLDBLU2    K+2     11    LOAD 6      115.00  1
 143623     0.51479E-04      0.10855E-02    CMLDBLU2    K       12    LOAD 7      115.00  1

Comments

Have you checked the log file for warnings on the CMLD models? These types of messages may exist: At bus 4, CMLD load bus voltage of 0.9471 pu is below 0.95 minimum. Original feeder Z of 0.2295 +j 0.2295 pu on SBASE will be reduced in an attempt to bring V up above 0.95 pu

GaryB gravatar imageGaryB (Apr 20 '3)

1 answer

Sort by » oldest newest most voted
0

answered Apr 20 '3

perolofl gravatar image

The problem is that governor at bus 3 (and maybe at bus 2) is hitting a governor limit. I.e. the generation (Pgen) in load flow is outside the limits defined in the governor model.

Adjust Pgen, solve and try again.

link

Comments

Hello, yeah I figured out it and could solve it. But I'm trying to solve the CMLDBLU2 models. Any comments to start with would be appreciated.

Erandika gravatar imageErandika (Apr 20 '3)

Didn't CMLDBLU2 messages disappear when you fixed the governor problems????

perolofl gravatar imageperolofl (Apr 20 '3)

No, I have mentioned a part of the initial conditions suspects in this post. There are about 70 of CMLDBLU2 suspects in the original log file. I'm doing this dynamic simulation for a large power system.

Erandika gravatar imageErandika (Apr 20 '3)

Just to be sure what you mean. Have you redone the inialisation after correcting generators at bus 2 and 3?

perolofl gravatar imageperolofl (Apr 20 '3)

Yeah, I did. I initialized the case after correcting the generators.

Erandika gravatar imageErandika (Apr 20 '3)