I have a transformer with 21 taps, +/-2.5% Voltage Variation.
How to compute R1min, R1max, Vmin, Vmax for the OLTC PSS/E model?
add a comment
First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
asked 2023-04-13 21:49:17 -0600
Anonymous
I have a transformer with 21 taps, +/-2.5% Voltage Variation.
How to compute R1min, R1max, Vmin, Vmax for the OLTC PSS/E model?
Use Winding I/O code 3:
R1max = 1 + 10*0.025 = 1.25
R1min = 1 - 10*0.025 = 0.75
Set voltage dead band to at least 2.5%*1.5 = 3.75%. For example Vmax = 1.01875 pu, Vmin = 0.98125 pu