Is it common for hydro generator governors to have a GMax beyond the powerflow PMax

asked 2023-02-22 19:44:19 -0600

boat14 gravatar image

updated 2023-02-22 19:47:26 -0600

Is it common for hydro generator governors to have a GMax beyond the powerflow PMax?

I often see turbine governors for hydro units (HYGOV for example) having a GMax set to 1.0 or slightly higher. If I understand correctly, the GMax, in this case, is refers to the machine's powerflow MVABase - not the powerflow PMax. As a result, a unit with a HYGOV operating at PMax would increase to the GMax (higher output the PMax) if there was an underfrequency event.

edit retag flag offensive close merge delete

1 answer

Sort by ยป oldest newest most voted
0

answered 2023-02-27 06:03:45 -0600

perolofl gravatar image

Gmax is the maximum gate opening in pu. Maximum gate opening is 1 pu, i.e. gmax should normally be set to 1 pu.

The turbine power, Pmech, is in pu Mbase, i.e. a different pu system. In HYGOV parameter qNL defines the turbine flow at zero turbine power, normally 0.08 - 0.1 pu flow. At steady state conditions (constant frequency) flow q has the same value as gate opening g.

The turbine gain, At and qNL, are used to convert the signal from pu flow to pu power. The following figure explains the relationship:

image description

Maximum Pmech: Pmaxpu = Pmax(MW)/Mbase(MVA).

The turbine gain At is used to match maximum Pmech to Gmax, using this formula:

At = Pmax/Mbase/(Gmax-qNL)

Example: Pmax 95 MW, Mbase 100 MVA, qNL = 0.1:

At = 95/100/(1-0.1) = 0.95/0.9 = 1.0555556

Parameter At is the slope of the line in the figure above.

Pmin in the figure just illustrates that the minimum turbine power in HYGOV is negative at zero gate opening (zero flow).

Here, gate opening 1 pu corresponds to (1-0.1)x1.0555556 = 0.95 pu Mbase = 95 MW, i.e. dynamic limit is the same as the load flow limit.

If Rsource > 0 for the generator the machine losses makes Pmech a little higher than 0.95 pu at maximum generation in load flow. The turbine gain should then be increased a little in order to avoid initialisation problems with HYGOV model.

So, Gmax = 1 is the correct limit in PSSE. Parameter At shall be calculated for each individual hydro generator.

===========================================================

Warning: PTI manual (PAG-II, chapter 18.5.2) presents the following "representive data" for HYGOV:

Gmax = 1, qNL = 0.08, At = 1.2

Here, maximum gate opening corresponds to Pmech = (1-0.08)x1.2 = 1.104 pu. For our generator that is 110.4 MW compared to maximum power 95 MW in load flow. Hence, the dynamic model may wrongly heavily overload the turbine at underfrequency situations.

There are more examples in the manual where PTI recommends too high dynamic limits for governor models. E.g. GAST model, here PTI recommend VMAX = 1 pu, which is wrong if Pmax < Mbase.

Many PSSE users worldwide are thereby using wrong power limits in their dynamic models.