Ask Your Question
0

Impedance Entry

asked 2023-02-18 10:40:02 -0600

anonymous user

Anonymous

I received the data in the following format. How to enter it in PSS/E? What is the W unit? Feeder sequence data R (W) X (W) B (uS)

edit retag flag offensive close merge delete

1 answer

Sort by ยป oldest newest most voted
0

answered 2023-02-20 09:56:42 -0600

Alex P gravatar image

I would double check with the provider of the info. To me, W is like w, which is like a lower case omega, and capital omega is of course the Ohm symbol. So I suspect R and X are in Ohms. uS are just the inverse of mega Ohms. Calculate your Zbase on the system voltage and 100 MVA and enter those values. The wikipedia page on per unit values is a good reference.

PSS/E technically does accept entering values in physical units (versus per unit values), but it's not really built for it and it gave me lots of strange trouble the one time I tried to use it with physical units.

edit flag offensive delete link more