How to fix the PF at the POI?

asked Jan 29 '3

anonymous user

Anonymous

How to fix the PF at the slack bus?

2 answers

Sort by » oldest newest most voted
0

answered Jan 31 '3

From your question I unsderstand you should be modelling a generation plant and trying to maintain reactive power/ power factor at POI.

You can set fixed Qgen for the generator (keep same value for both Qmax, Qmin) and with iterative method you can adjust this acheive required reactive power corresponding to that powerfactor.

Or other way would be you can adjust Voltage of the generator to control the reactive power flow at POI.

link
0

answered Jan 30 '3

perolofl gravatar image

The slack bus generator will always inject the necessary Mvar to keep the scheduled voltage. Adjust the Mvar injection by nearby generators, fixed shunts, switched shunts, FACTS, etc., in order to change Qgen of the slack bus.