how to change the P at the slack POI bus?
asked 2023-01-28 18:08:19 -0600
Anonymous
I have a system with a fixed voltage and PF at the POI. How do I change the injected POI power from 0% to 100%?
First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
asked 2023-01-28 18:08:19 -0600
Anonymous
I have a system with a fixed voltage and PF at the POI. How do I change the injected POI power from 0% to 100%?
From your question I unsderstand you should be modelling a generation plant and trying to control power flow at POI.
The answer is, You have to set Pgen on your generators to change your power at POI from 0 to 100% Additionally to maintain fixed power factor you also need to adjust Qgen or V pu accordingly to control reactive power at POI
It is not clear what you want, but I assume you should change the active power generation (Pgen) in your ”system”.
Asked: 2023-01-28 18:08:19 -0600
Seen: 191 times
Last updated: Jan 31 '23