Voltage Negative Sequence in dynamic studies

asked Apr 24 '2

dvit gravatar image

Hello,

I have the understanding that under a dynamic simulation PSSE calculates the positive sequence matrix and performs and the generator is also represented in the positive sequence. This situation works great with balanced faults.

However, with unbalanced faults under a dynamic simulation PSSE does not permit to read the negative sequence voltage at the generator terminals until PSSe 34.7. Is this correctly understood?

Unfortunately, I am not able to find evidence in the manual of confirmation or denying of my question in the manual.

Thus, I would also to like to ask if anyone knows where this information is written in the manual? Thank you.

1 answer

Sort by » oldest newest most voted
0

answered May 6 '2

GaryB gravatar image

The dynamic models are positive sequence only. It's possible to run unbalanced fault (at least SLG), but PSSE still only simulates the positive sequence. You cannot read negative sequence values because they aren't simulated.

I assume short-circuit analysis simulates negative and zero sequences. The detrimental effects of negative sequence happen during a fault. I would use short-circuit analysis and known breaker timings.