Ask Your Question
0

Grid forming inverter implementation

asked 2022-04-04 22:13:16 -0600

powerengineer gravatar image

Hi everyone, I want to implement grid-forming inverters in PSS/E to analyze their impact on system stability. I have some experience with grid-following inverters using REGCA1, REECA1, and REPCA1. Can anyone please guide me how to implement a grid-forming inverter?

Thank you.

edit retag flag offensive close merge delete

1 answer

Sort by ยป oldest newest most voted
0

answered 2022-04-08 12:10:47 -0600

PSSE_Learner gravatar image

As far as i know, PSSE can not simulate an island network or in other words a V/F control can not work in PSSE. One way would be that the GFC stays connected with atleast one synchronous machine but then you can not do the V/F control effectively but if you remove machine, the simulation will probably not converge.

edit flag offensive delete link more