Ask Your Question
0

Short circuit data not showing in PSSE V33 and V34

asked 2021-11-04 15:29:52 -0600

Frank gravatar image

updated 2021-11-04 15:48:22 -0600

Hi, I downloaded PSSE a few months ago so I am still fairly new. When I open a .sav case, and clicked on a branch in the single line diagram, I am unable to see the "Short Circuit" tab (to the right of the "Power Flow" tab). As well, the zero sequence columns in the .sav file are empty. This problem can be seen for multiple .sav cases

Does anyone know what this might be caused by? Thanks

edit retag flag offensive close merge delete

1 answer

Sort by ยป oldest newest most voted
0

answered 2021-11-04 15:48:22 -0600

perolofl gravatar image

It seems like your case only contains positive sequence data. Sequence data with zero sequence impedance are not added to your saved case.

edit flag offensive delete link more

Comments

if you open the savnw.sav case (located in the example folder), you'll see such data.

jconto gravatar imagejconto ( 2021-11-04 16:38:00 -0600 )edit

Thanks for your response, but after using the example case savnw.sav from the tutorial (https://www.youtube.com/watch?v=FG3MzRy2Sqo) the short circuit tab (1:12 in the video) doesn't show up for me

Frank gravatar imageFrank ( 2021-11-04 16:44:00 -0600 )edit

Use the savnw.sav file in the PSSe installation folder "example", default path:"C:\Program Files (x86)\PTI\PSSE34\EXAMPLE\savnw.sav"

jconto gravatar imagejconto ( 2021-11-04 18:45:26 -0600 )edit