What is X Source in Generator Model ?

asked Jul 27 '1

Awab Alameen gravatar image

I have some doubts about the X Source in Generator Model, is it Xd' or some thing else ?

1 answer

Sort by » oldest newest most voted
0

answered Jul 28 '1

lmcqueen gravatar image

The Xsource in the generator power flow model is the unsaturated subtransient reactance in p.u. Please refer to PAGV1.pdf for more information about the generator model.

link

Comments

Thanks for replying. Why it is in steady state generator tab ?

Awab Alameen gravatar imageAwab Alameen (Jul 28 '1)

In PSS/E, the power flow model is linked with the dynamic model. The PSS/E checks for the value of Xsource in the power flow to see if it is the same as the X" in the generator dynamic model.

lmcqueen gravatar imagelmcqueen (Jul 28 '1)

It's also used in short circuit calculations.

likethevegetable gravatar imagelikethevegetable (Jul 29 '1)

The unsaturated subtransient reactance cannot be used for short-circuit calculations.

lmcqueen gravatar imagelmcqueen (Jul 30 '1)

How else would the generator impedance be modelled for short circuit contribution?

likethevegetable gravatar imagelikethevegetable (Jul 30 '1)