PV model in PSS/E

asked 2021-06-14 07:50:02 -0500

dsam gravatar image

Hello, I want to integrate a PV in a network in PSS/E. When I go to choose the generator of the renewable machine in .dyr file, it appears to choose between the following models: WT1G1, WT2G1, WT3G1, WT3G2, WT4G1, WT4G2. I use PSS/E 33 version. What generator should i choose to integrate a PV?

edit retag flag offensive close merge delete

1 answer

Sort by ยป oldest newest most voted
1

answered 2021-12-02 09:45:41 -0500

Tran Huu Phuc gravatar image

The model suitable the most for PV in PSS/E 33 version is PVGU, PVEU, PANEL and IRRAD. Here is the sample model from PAGV2 form PTI DOCS.

5 'USRMDL' 1 'PVGU1' 101 1 0 9 3 3
0.20000E-01 0.20000E-01 0.40000 0.90000
1.1100 1.2000 2.0000 2.0000 0.20000E-01 /
5 'USRMDL' 1 'PVEU1' 102 0 4 24 10 4
5 0 1 0
0.15000 18.000 5.0000 0.50000E-01 0.10000
0.0000 0.80000E-01 0.47000 -0.47000 1.1000
0.0000 0.50000 -0.50000 0.50000E-01 0.10000
0.90000 1.1000 120.00 0.50000E-01
0.50000E-01
1.7000 1.1100 1.1100 10.0/
5 'USRMDL' 1 'PANELU1' 103 0 0 5 0 1
0.16 0.38 0.59 0.85 1 /b
5 'USRMDL' 1 'IRRADU1' 104 0 1 20 0 1
1
5 1000 10 900 15 850 20 800 25 700
30 600 35 700 0 0 0 0 0 0 /