Problem in initilization

asked 2021-06-06 10:59:17 -0600

dsam gravatar image

When i replace a generator in IEEE-24 bus with a WT4 wind turbine and i do initilization it appears this problem:

Model IEEEX1 Bus 7 [BUS7 138.00] Machine "1 " : initialized out of limit(s) VR

Model IEEEX1 Bus 16 [BUS16 230.00] Machine "1 " : initialized out of limit(s) VR

Model IEEEX1 Bus 23 [BUS23 230.00] Machine "1 " : initialized out of limit(s) VR

Model IEESGO Bus 7 [BUS7 138.00] Machine "1 " : initialized out of limit(s) PMECH(I) CONTROL WT4E1 AT BUS 13 MACHINE 1 WRONG INITILIZATION: ACTIVE NET CURRENT 1.2663 EXCEEDS MAXIMUM 1.1100

How i can solve this problem? Thank you.

edit retag flag offensive close merge delete

1 answer

Sort by ยป oldest newest most voted
0

answered 2021-06-07 04:00:43 -0600

perolofl gravatar image

It seems like the change to wind generator changed the load flow and other generators became overloaded in reactive power.

Is bus 7 swing bus? Bus 7 has a PGEN outside the power limits in model IEESGO.

Did you replace generator at bus 13? It seems like the generator is overloaded.

edit flag offensive delete link more

Comments

No the swing bus is 1 bus. Yes i replace the bus 13 with a wind generator.

dsam gravatar imagedsam ( 2021-06-07 07:04:47 -0600 )edit

Is PGEN at bus 7 changed? Is it the same PGEN and QGEN at bus 13 after changing to wind generator?

perolofl gravatar imageperolofl ( 2021-06-07 13:18:12 -0600 )edit