Tap positions
When I change tap postion in stady state mode nothing happend. I add controlled bus number an put control mode 1- Voltage, but when I change tap position, voltage dont change.
Does anyone now why?
First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
When I change tap postion in stady state mode nothing happend. I add controlled bus number an put control mode 1- Voltage, but when I change tap position, voltage dont change.
Does anyone now why?
Asked: 2021-04-16 01:45:29 -0600
Seen: 565 times
Last updated: Apr 16 '21
Voltage calculation for nodes in a weighted undirected graph
How can you get the values of the sensitivity matrix?
Weather in PV analyis,is it possible for practical grid to have voltage almost near to 1pu?
Extract Bus Voltage Magnitude and Angle from .sav case
API for changing tap position in dynamic simulation
Request, Online Tap Changer Example
What do you change? There is no parameter for ”tap position”.
To simulate a tap position change you would need to change the winding voltage for the transformer winding that has the tap.