Ask Your Question
0

PV analysis .sub file

asked 2021-04-05 13:10:30 -0500

OK gravatar image

I am trying to perform PV analysis but I am getting error: Messages for api PVENGINE1A No participating dispatch busses in opposing system "SINK" {000189}. I already defined a source and a sink in my .sub file but still I have the same problem. I tried to use in sink an existing area and it works, but I don't want to increase the load of this area, instead I want to increase the load of specific Zone, but I am facing this issue. Please help

edit retag flag offensive close merge delete

2 answers

Sort by » oldest newest most voted
0

answered 2021-04-05 22:36:57 -0500

OK gravatar image

updated 2021-04-06 11:03:22 -0500

jconto gravatar image

Yes I used the same zone number as the load, but still facing same problem. Please find below .sub file:

Subsystem SOURCE
Zone 911
end
Subsystem SINK
Zone 221
end
Subsystem 132_Network
JOIN Group1
Area 8
Owner 433
end
end
Subsystem my_network
JOIN Group2
Area 9
Owner 443
end
end
Subsystem Yoga_plant
BUS 772
BUS 777
BUS 782
end
Subsystem Moka_plant
BUS 622
BUS 627
BUS 632
end
end
edit flag offensive delete link more

Comments

Hi, please check if the sink you specified has in-service generators.

lmcqueen gravatar imagelmcqueen ( 2021-04-06 07:31:17 -0500 )edit

No my sink does not have any generators, I think sink represents the load bus, which I want to increase its power. While source should contain the generators? Is my understanding correct?

OK gravatar imageOK ( 2021-04-06 07:34:33 -0500 )edit

There should be generators in both subsystems. For Source Subsystem, the generators you specify there will increase their dispatch while recognizing its limits. For the Sink Subsystem, the generators will decrease their output.

lmcqueen gravatar imagelmcqueen ( 2021-04-06 07:48:27 -0500 )edit

Maybe my understanding is wrong, but why would we need to reduce generation from sink side? We just want to examine how much power can be delivered to specific substation, wh ْ.ْ ile increasing its power until we face voltage collapse, this is the definition of PV analysis right?

OK gravatar imageOK ( 2021-04-06 07:54:09 -0500 )edit

The reduction of generation in the Sink subsystem is for the purpose of balancing the generation-demand of the power system.

lmcqueen gravatar imagelmcqueen ( 2021-04-06 09:01:46 -0500 )edit
0

answered 2021-04-05 13:29:33 -0500

jconto gravatar image

Can you post the SUB file?

Source and Sink regions (areas, zones, or any grouping combination allowed) have unique elements. Also check that the zone number exists in the case and it contains loads. Remember that load's zones numbers may be different than its bus zone numbers.

edit flag offensive delete link more

Comments

Please refer to above answer, as it is not possible to reply here as a comment

OK gravatar imageOK ( 2021-04-05 22:41:14 -0500 )edit

Make sure on main PV menu, in section "Transfer dispatch methods" -> "For opposing sink system", select DFAX load.

jconto gravatar imagejconto ( 2021-04-06 11:34:36 -0500 )edit

Yes thats what I selected, PV worked for me after inserting some generation at sink zone, but I got another issue, where the PV analysis is not really reflecting how much power can certain zone handle before it collapses. Where, the PV stopped increasing at 250MW.. continue next comment.

OK gravatar imageOK ( 2021-04-07 11:05:16 -0500 )edit

but later I increased the load manually and I was able to increase even up to 600 MW without problem

OK gravatar imageOK ( 2021-04-07 11:05:38 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

[hide preview]

Question Tools

1 follower

Stats

Asked: 2021-04-05 13:10:30 -0500

Seen: 460 times

Last updated: Apr 06 '21