how is Vref in REPCAU1 (VAR L) calculated?
Hello - after initializing my case I noticed that VAR L in REPCAU1 model (Vref) takes a value that I am not able to match to the any bus voltage. My question is: where does this value come from?
First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
Hello - after initializing my case I noticed that VAR L in REPCAU1 model (Vref) takes a value that I am not able to match to the any bus voltage. My question is: where does this value come from?
Maybe you are using line drop compensation, i.e. Rc and Xc are not 0.
Asked: 2021-03-24 10:33:09 -0500