what does 'VTGDCAT' mean in renewable models.
I want what V - stands for T - stands for G - stands for D - stands for C - stands for A - stands for T - stands for
First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
I want what V - stands for T - stands for G - stands for D - stands for C - stands for A - stands for T - stands for
It's an under-voltage generator bus disconnection relay.
Here's my interpretation.
VTG -> Voltage DCAT -> "Disconnect at" (disconnect the bus where the generator is at, meaning that all equipment at the bus is tripped)
This is in contrast to the VTGTPAT model VTG -> Voltage TPAT -> "Trip at" (only trips the generator and does not disconnect the bus)
It's a little bit cryptic admittedly, but welcome to PSS/E!