Ask Your Question
0

Difference between Connection code 9 and 20 (Zero Sequence)

asked 2020-10-11 17:21:49 -0500

Arcangel_PQ gravatar image

Using ODMS10 model to extract a PSSe v32 file (Raw and seq), however when I open it in PSSe 34 Some Ynyn0 transformers extract as Connection code (CC) 9, but the program suggests it should be (in the vector group) CC 20. What is the zero sequence difference between these two CCs, as it isn't discussed in the PSSe manual.

I tried testing the same transformer in a basic Gen + Transformer + Load model. When I fault the LV bus it get a different earth fault for the two CCs. (results below

  • Connection Code 9

X------------ BUS ------------X PU PU 40085 [XXXXX 33.000] 3PH 0.99 0.0781 -0.9906 LG 1.10 -0.1287 -1.0884 THEVENIN IMPEDANCE, X/R (PU) Z+:0.806215+j0.634362, 0.78684 Z-:0.806215+j0.634362, 0.78684 Z0:0.201859+j0.851560, 4.21859

  • Connection Code 20

X------------ BUS ------------X PU PU 40085 [XXXXX 33.000] 3PH 0.99 0.0781 -0.9906 LG 1.41 0.0242 -1.4112 THEVENIN IMPEDANCE, X/R (PU) Z+:0.806215+j0.634362, 0.78684 Z-:0.806215+j0.634362, 0.78684 Z0:0.004812+j0.173282, 36.01337

The short circuit CC drop down menu identifies 9 as "Series path on each side, ground path at junction (auto) and 20 as "Series path on each side, ground path at junction".

Now I understand that from v33 onwards the zero sequence model for the CCs was expanded and I'm wondering if this is why the earth fault and zero sequence Thevenin equivalent model so different?

Regards,

Andrew

edit retag flag offensive close merge delete

1 answer

Sort by ยป oldest newest most voted
0

answered 2020-10-12 02:38:37 -0500

perolofl gravatar image

Have you read Chapter 5.5.5 in Program Operation Manual?

edit flag offensive delete link more

Comments

Just checked the POM - it only goes upto 5.5.2 and then it is section 5.6. POM PSSe 34.7.0

Arcangel_PQ gravatar imageArcangel_PQ ( 2020-10-12 15:28:29 -0500 )edit

I have rev 34.6.0. The Chapter is titled:"5.5.5. Two Winding Transformer Zero Sequence Network Diagrams and Connection Codes". Seems to be missing in rev 34.7.0. Contact Siemens PTI!!!

perolofl gravatar imageperolofl ( 2020-10-13 02:13:21 -0500 )edit

I've got a conference call scheduled with them for Thu - but thought I'd try seeing if anyone else had experience with this. What I have found out is that it partly comes down to whether you are modelling the transformer as Shell type or Core type. Seeking further clarification.

Arcangel_PQ gravatar imageArcangel_PQ ( 2020-10-13 17:18:59 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

[hide preview]

Question Tools

1 follower

Stats

Asked: 2020-10-11 17:21:49 -0500

Seen: 500 times

Last updated: Oct 12 '20