Vestas 850 kW 50 Hz LVRT Undervoltage Trip

asked 2020-09-30 22:51:44 -0500

ffl gravatar image

I am performing dynamic simulation with several Vestas 850 kW WTG Units. I keep on receiving an error "LVRT Undervoltage trip at time 0.1917 s". This is just after initialization. The parameters of the vestas dynamic model is based on the model documentation. The load flow conditions are ok: terminal voltage at the WTG bus is within the nominal value.

What could be the reason for this error?

edit retag flag offensive close merge delete

Comments

This sounds like a question to ask Vestas.

jfconroy gravatar imagejfconroy ( 2020-10-01 02:24:22 -0500 )edit

That's what I'm thinking too. Just checking out if someone experienced this issue. Anyway thank you for replying.

ffl gravatar imageffl ( 2020-10-01 08:48:54 -0500 )edit

It's very difficult to answer a question such as yours without having access to your files to replicate the issue. Vestas are usually quite helpful if you're working on one of their projects.

jfconroy gravatar imagejfconroy ( 2020-10-02 04:29:51 -0500 )edit

1 answer

Sort by » oldest newest most voted
0

answered 2020-10-26 02:49:31 -0500

perolofl gravatar image

Do you have a channel with the terminal voltage? Does the voltage decrease in the simulation or is it constant? What are the settings for the undervoltage relay?