Network not converged at TIME = -0.02 despite initial conditions check being okay

asked Sep 8 '0

abdul gravatar image

I have a network that works just fine in load flow studies. However, when I run dynamic simulation, the network does not converge right after initialization despite showing initial conditions check being okay. Since there are no initial conditions suspects, I find it hard to troubleshoot. Please help.

1 answer

Sort by » oldest newest most voted
0

answered Sep 9 '0

perolofl gravatar image

Activate the convergence monitor at initialization. You will then see which bus has the largest mismatch.

link