frecuency recovery after an event - isochronous control

Hi all,

I am trying to perform a simulation of a restoration process: Starting from a generator + load energize the whole system.

So when i connect a generator or a load, after the transitory period the frequency stabilizes in a level (under o over nominal) and I want that frequency to come back to normal. So the primary frequency control is working but not the secondary.

I've tried PLVFU1, using R=0 for the governor and the GGOV1 with control mode 0 (=isochronous) withiout success.

Any recommendation?

Thanks in advance

alejanpato's avatar
3
alejanpato
asked 2020-05-28 05:39:22 -0500
edit flag offensive 0 remove flag close merge delete

Comments

Don't use PLVFU1 here. Have you tested with a normal generator model and governor model GGOV1? Which parameters have GGOV1?

perolofl's avatar perolofl (2020-05-28 07:21:31 -0500) edit

I have actually managed with GGOV1 using R=0 and isochronous control. Thank you

alejanpato's avatar alejanpato (2020-05-28 07:31:56 -0500) edit