REPCTA1 model in PSSE
The slope setting in PPC operating in Voltage control is reflected by which CON value/s of REPCTA1 model? eg. if the slope setting is changed from 0.1 to 0.05 in PPC at site, how to reflect the same in PSSE. Thanks in advance
First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
The slope setting in PPC operating in Voltage control is reflected by which CON value/s of REPCTA1 model? eg. if the slope setting is changed from 0.1 to 0.05 in PPC at site, how to reflect the same in PSSE. Thanks in advance
I agree with the previous comment, it is good practice to check the MODELS documentation to get accustomed to the PSSE models of interest. However, I believe the parameters you are looking for are Kp and Ki; the proportional and integral gains for the reactive power control PI control.
Hope that helps.
There should be a documentation folder with PSSE or in the Start Menu. What you are looking for is in there.
Asked: 2020-05-27 02:37:10 -0600
Seen: 456 times
Last updated: Jun 03 '20
Thanks , But for the benefit of all, the CON value Kc defines the slope setting for PPC in voltage control Regards