How to increse the electrical power

asked May 25 '0

Mostafa.kandil gravatar image

Hi all, I'm doing Dynamic simulation for BESS on IEEE 9 bus system. the problem now that the system is fully depending on the power from the BESS so once it's energy is drained it collapse to instability. So I need to know how to increase the active power from the conv. machine to compensate the BESS and system remain stable. I'm using governor model IEESGO and LCFB1 but still I have Freq. Deviation. Any ideas?

2 answers

Sort by » oldest newest most voted
0

answered May 29 '0

yunzhi cheng gravatar image

To bring frequency back to 60Hz, you need a AGC model

link

Comments

LCFB1 is an AGC model!!!

perolofl gravatar imageperolofl (May 29 '0)
0

answered May 25 '0

perolofl gravatar image

Test first if model LCFB1 is correctly implemented. Does it update VAR(L) of IEESGO model?

link

Comments

Yes it does I checked V (L+2) in LCFB model and V(L) in IEESGC and both are the same

Mostafa.kandil gravatar imageMostafa.kandil (May 26 '0)

Yes, but is VAR(L) of IEESGO changed during the simulation? Or is the signal constant?

perolofl gravatar imageperolofl (May 26 '0)

how to know?, shall I draw this one during the simulation and check?

Mostafa.kandil gravatar imageMostafa.kandil (May 26 '0)

Put the var in a channel and plot.

perolofl gravatar imageperolofl (May 26 '0)

I plot the VAR (L) and It's a constant value during the simulation, no changes. Dose it mean that the LCFB is not functioning correct? if so how to fix it?

Mostafa.kandil gravatar imageMostafa.kandil (May 26 '0)