REPCAU reference set point

asked 2020-05-25 05:04:45 -0600

pff gravatar image

In the REPCA model Vref=Vreg+Kc*Qbranch(pu) [1] with RfFlag=1 I have to do the following test: verifying model responds to the voltage reference set point step test from 1.0146 pu to 1.0222 pu at POI bus. Initialy (flat start) Vref=1.0142 due to the ecuation 1 (instead of the LF voltaje 1.0146). If I want to increase the reference setpoint to 1.022, how should I change VAR(L)?

edit retag flag offensive close merge delete

1 answer

Sort by » oldest newest most voted
0

answered 2020-05-26 00:49:46 -0600

perolofl gravatar image

At initialization, Vref = Vt+Kc*Qbranch.

During simulation, Verror = Vref-(Vt+Kc*Qbranch).

You want to make a step test from 1.0146 to 1.0222 pu. That is an increase with factor 1.00749.

With the actual Q loading of the plant and the chosen droop factor Kc, Vref shall be changed from 1.0142 to 1.0142*1.00749 = 1.0218.

Please note that due to the dróop Kc, the actual voltage will not reach 1.0222 pu.