What is the difference in results between the AC contingency Solution (ACCC) method and the N-R solution Governor Redispach method

asked Apr 23 '0

Juan gravatar image

updated Apr 29 '0

What is the difference in results between the AC contingency Solution (ACCC) method and the N-R solution Governor Redispach method

in one method before the same contingency it gives me 59% overload and in the other it gives me 85%

image description

Comments

Have you read in the manual?

perolofl gravatar imageperolofl (Apr 23 '0)

1 answer

Sort by » oldest newest most voted
0

answered Apr 25 '0

perolofl gravatar image

In a normal solution (FNSL, ACCC, etc.) the swing bus takes up the MW mismatch. Normally you have only one swing, so the whole MW error will be compensated by one plant.

Solving with inertial/governor dispatch (INLF) means that the power taken up by the swing will be redistributed to all generators according the their MVA size (MBASE). This will of course lead to a different load flow in the network.

Solving with INLF (Governor response) is a way to study the effect of primary frequency control without performing a dynamic simulation.

link

Comments

thanks, What you say is correct, However in the PSSE 33.5, it gives you the option to do the simulation with a governor response, defining a dispatch subsystem, where it is supposed to distribute the mismatch in all the machines of that without their subsystem the answers always differs

Juan gravatar imageJuan (Apr 29 '0)