Type 4 Wind turbine in PSS/E

asked 2020-04-22 08:38:42 -0600

anonymous user

Anonymous

Excuse me, My wind turbine has been set to Generator Bus. Why my voltage is not 1pu (0.996pu) before the three-phase to ground fault, which makes my wind turbine need reactive power compensation at the beginning.

edit retag flag offensive close merge delete

1 answer

Sort by » oldest newest most voted
0

answered 2020-04-25 03:58:37 -0600

perolofl gravatar image

A type 4 wind turbine has a large reactive power capability, so any additional compensation is hardly needed. Which Control Mode have you chosen for the wind machine?

edit flag offensive delete link more

Comments

I choose Q priority.

Kevin gravatar imageKevin ( 2020-04-29 01:57:54 -0600 )edit

I mean in the saved case data, tab Machine, column Wind machine Control Mode.

perolofl gravatar imageperolofl ( 2020-04-29 03:32:10 -0600 )edit

you mean code number right? I set wind machine as generator bus(code 2).

Kevin gravatar imageKevin ( 2020-04-29 20:47:03 -0600 )edit

No! In generator data there is a code for "Wind machine Control Mode" (WMOD). Read the manual!

perolofl gravatar imageperolofl ( 2020-04-30 02:57:09 -0600 )edit

sorry,I didn't understand until now. I choose (Renewable: Standard QT, QB limits)

Kevin gravatar imageKevin ( 2020-04-30 06:31:21 -0600 )edit

And which limits have you chosen for Qmax and Qmin?

perolofl gravatar imageperolofl ( 2020-04-30 07:35:25 -0600 )edit

I set 1.051Mvar(Qmax) and -1.051(Qmin)

Kevin gravatar imageKevin ( 2020-05-01 08:03:37 -0600 )edit

if I set it as zero,the code number will change it to -2.

Kevin gravatar imageKevin ( 2020-05-01 08:05:01 -0600 )edit

can you connect me with file ,i can show you file. Thank you! (kevinhuang85316 ) for gmail

Kevin gravatar imageKevin ( 2020-05-01 22:36:52 -0600 )edit

Code -2 means that the generator has hit a reactive power limit (Qmax or Qmin). The bus voltage may then deviate from the scheduled voltage. This is why your voltage is 0.996 instead of 1 pu.

perolofl gravatar imageperolofl ( 2020-05-04 04:53:15 -0600 )edit

I know what you are saying. But in normal operation, wind turbine voltage should be 1 p.u. right? why my wind turbine need reactive power without any fault

Kevin gravatar imageKevin ( 2020-05-04 06:46:17 -0600 )edit