Type 4 Wind turbine in PSS/E
Excuse me, My wind turbine has been set to Generator Bus. Why my voltage is not 1pu (0.996pu) before the three-phase to ground fault, which makes my wind turbine need reactive power compensation at the beginning.
First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
Excuse me, My wind turbine has been set to Generator Bus. Why my voltage is not 1pu (0.996pu) before the three-phase to ground fault, which makes my wind turbine need reactive power compensation at the beginning.
A type 4 wind turbine has a large reactive power capability, so any additional compensation is hardly needed. Which Control Mode have you chosen for the wind machine?
Asked: 2020-04-22 08:38:42 -0600
Seen: 1,859 times
Last updated: Apr 25 '20
whit loves you. Content on this site is licensed under a Creative Commons Attribution Share Alike 3.0 license.