Ask Your Question
0

Type 4 Wind turbine in PSS/E

asked 2020-04-22 08:38:42 -0500

anonymous user

Anonymous

Excuse me, My wind turbine has been set to Generator Bus. Why my voltage is not 1pu (0.996pu) before the three-phase to ground fault, which makes my wind turbine need reactive power compensation at the beginning.

edit retag flag offensive close merge delete

1 answer

Sort by ยป oldest newest most voted
0

answered 2020-04-25 03:58:37 -0500

perolofl gravatar image

A type 4 wind turbine has a large reactive power capability, so any additional compensation is hardly needed. Which Control Mode have you chosen for the wind machine?

edit flag offensive delete link more

Comments

I choose Q priority.

Kevin gravatar imageKevin ( 2020-04-29 01:57:54 -0500 )edit

I mean in the saved case data, tab Machine, column Wind machine Control Mode.

perolofl gravatar imageperolofl ( 2020-04-29 03:32:10 -0500 )edit

you mean code number right? I set wind machine as generator bus(code 2).

Kevin gravatar imageKevin ( 2020-04-29 20:47:03 -0500 )edit

No! In generator data there is a code for "Wind machine Control Mode" (WMOD). Read the manual!

perolofl gravatar imageperolofl ( 2020-04-30 02:57:09 -0500 )edit

sorry,I didn't understand until now. I choose (Renewable: Standard QT, QB limits)

Kevin gravatar imageKevin ( 2020-04-30 06:31:21 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

[hide preview]

Question Tools

1 follower

Stats

Asked: 2020-04-22 08:38:42 -0500

Seen: 1,366 times

Last updated: Apr 25 '20