Ask Your Question
0

How do I convert a 3-winding transformer series impedance into per unit impedance for PSSE

asked 2020-03-15 09:51:20 -0500

tharinda11 gravatar image

3 winding transformer, given data

HV 0.58+j62, MV 0.39, LV 2.9+j119

HV: MV 525/230 kV

HV: LV 525/11 kV

100MVA base

edit retag flag offensive close merge delete

1 answer

Sort by ยป oldest newest most voted
0

answered 2020-03-17 13:42:55 -0500

drsgao gravatar image

I remember that one of the manuals, probably one of the 2 about the models, describes the transformer models in PSSE and how you could convert the Ohmic values into the per-unit one. You need to know how the transformer is physically connected (the clock).

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

[hide preview]

Question Tools

1 follower

Stats

Asked: 2020-03-15 09:51:20 -0500

Seen: 1,804 times

Last updated: Mar 17 '20