asked 2019-11-24 02:35:51 -0600

Jai gravatar image

Dear All,

I am facing wierd problem. When I perform load flow, the model converges and gives proper results. When I checked "Report>Area/owner/zone totals", the load values present in this report and actual value of load (which are switched on) in the load columns in Network Data are different. For e.g. in the load column the total value of load is : 1200 MW and when I generate report the load value ( "TO LOAD) column comes to 700 MW. I dont know why there is a difference between these two values. In my understanding, these both values should match.

I woudl really appreciate if any one you knows how to solve the problem. Thank you in advance.

Kind Regards, Jai

edit retag flag offensive close merge delete

1 answer

Sort by ยป oldest newest most voted
0

answered 2019-11-25 02:14:41 -0600

perolofl gravatar image

The report only shows in-service loads at in-service buses. Some load buses are out of service, i.e. bus code = 4.