Has anyone got a typical parameters for LCFB1 Model?
Turbine load-controller model
This free publication contains typical values for model LCFB1: http://sites.ieee.org/fw-pes/files/20...
Thank you very much@jconto. I am actually trying to get a secondary frequency response with LCFB1 model. With the PLBVFU1 model I couldn't get the GT's frequency response - it just follows the PLBVFU1 model but no response. Any thoughts would be much appreciated.
The PLBVFU1 model sets the f and v at the PLBVFU1 generator. The frequency would be the same over the network, while the voltage would change along it. The GT frequency channels will of course follow the f set by the PLBVFU1 mode but its Pout would change according to its governor dynamics.