how can i apply a purely reistive fault in PSS/E or is it possible?

asked Jun 24 '19

Sazzad gravatar image

I need this for SMIB study for grid connection

1 answer

Sort by » oldest newest most voted
1

answered Jun 24 '19

perolofl gravatar image

It is just to enter a resistive fault admittance, i.e. G>0 and B=0.

Example: A resistive shunt of 500 MW:

psspy.dist_bus_fault(ibus,1,0.0,[ 500.0,0.0])

A resistance of 10 ohm:

psspy.dist_bus_fault(ibus,3,0.0,[ 10.0,0.0])