Ask Your Question
0

What is the base value used for the PMAX and PMIN values in REECB1 and REPCA1

asked 2019-06-12 17:43:37 -0500

bikiran1991 gravatar image

In the MODELS book, it says that these values are specified in pu (base). I am confused whether this means the system base or the generator MVA base.

Looking forward to learning the correct answer.

edit retag flag offensive close merge delete

2 answers

Sort by ยป oldest newest most voted
1

answered 2019-06-13 00:36:51 -0500

perolofl gravatar image

The values are in generator MVA base.

edit flag offensive delete link more

Comments

Does these models have any default parameters for like Kp or Ki wich represent PI control proportional and integral gains ? If yes, where is it ? I investigated through PAG1 and PAG2 and found nothing about it.

Diogo Carrilho gravatar imageDiogo Carrilho ( 2020-04-15 18:18:41 -0500 )edit
0

answered 2020-05-19 18:14:23 -0500

pk gravatar image

Kp & Ki parameter is available in REPCA1 ,J+1 , J+2. You can tune it as per your requirement

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

[hide preview]

Question Tools

1 follower

Stats

Asked: 2019-06-12 17:43:37 -0500

Seen: 526 times

Last updated: May 19 '20