Ask Your Question
0

How to change voltage angle in dynamic simulation

asked 2018-10-23 04:24:59 -0500

kamjays gravatar image

Consider SLD with single machine infinite bus, changing magnitude of the voltage in dynamic simulation can be done by changing Vref of Infinity machine. Or, it can be done by changing transformer tap. Question is: How to make voltage angle change ? (for example change 20° in step)

Thanks,

edit retag flag offensive close merge delete

Comments

I don't understand. In a dynamic simulation the voltage angle is a result at each time step and not input data that can be changed by the user.

perolofl gravatar imageperolofl ( 2018-10-23 06:25:19 -0500 )edit

I want to test generator behavior if there is voltage angle changes in the grid.

kamjays gravatar imagekamjays ( 2018-10-23 06:36:22 -0500 )edit

1 answer

Sort by » oldest newest most voted
0

answered 2018-10-23 08:16:35 -0500

perolofl gravatar image

Change the phase shift of the generator step-up transformer with 20 degrees. For example use API:

psspy.two_winding_chng_4(3008,3018,r"""1""",[],[_f,_f,_f,_f,_f, 20.0])

to change for generator at bus 3018 in savnw.sav.

edit flag offensive delete link more

Comments

thanks so much

kamjays gravatar imagekamjays ( 2018-10-23 09:33:41 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

[hide preview]

Question Tools

2 followers

Stats

Asked: 2018-10-23 04:24:59 -0500

Seen: 906 times

Last updated: Oct 23 '18