How to model a current limiting reactor in PSS/E?

asked 2018-01-18 23:10:38 -0600

Manu gravatar image

I want to reduce 3-phase fault MVA at 33kV Wind farm substation. I tried for split bus arrangement, but still the Fault MVA is not in recommended range. Can anybody suggest me how to model a current limiting reactor in PSS/E for this purpose?

edit retag flag offensive close merge delete

1 answer

Sort by ยป oldest newest most voted
0

answered 2018-01-20 07:10:54 -0600

jconto gravatar image

A "current limiting" reactor is still a reactor, modeled in steady state with its reactance in series with the branch connected to. Start with an initial value (10% of X of branch connected to),perform a short-circuit study and move it up or down until the allowed fault MVA is achieved.