vector group Yd5

asked 2017-07-04 15:49:02 -0500

Patricio1285 gravatar image

Greetings,

I'm modeling a simple power system: generator, transformer and load. The problem comes up after I enter the transformer's (Yd5) vector group. When doing this, at the time I run the load flow, there is the following response: "Blown up after 1 iteration". On the other hand, when I omit the vector group, the load flow's result is as expected. Has anyone had the same inconvenience?

edit retag flag offensive close merge delete

1 answer

Sort by ยป oldest newest most voted
0

answered 2017-07-05 01:08:38 -0500

perolofl gravatar image

updated 2017-07-05 06:14:27 -0500

Vector group Yd5 means 150 degrees phase shift between the two windings. This angle difference it too large as starting point for Newton-Raphson. Solve first with Gauss-Seidel and then continue with Newton!