First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!

Ask Your Question
0

How can i model using WSIEG1

asked May 29 '17

anonymous user

Anonymous

Hello,

I want to model using WSIEG1. I heard it is similar with IEEEG1. So, I modeled it using IEEEG1 parameters. However, the result is inital conditions suspect as follow:

I DSTATE(I) STATE(I) MODEL STATE 8018 -2.6906 0.80719 WSIEG1 K+2

How can I solve this problem?

I want to test for dead band of generators

1 answer

Sort by ยป oldest newest most voted
0

answered May 29 '17

oppossumX gravatar image

Were you able to successfully initialize the IEEEG1 model using the same data as your WSIEG1 model?

Have you entered any Deadband, NGV, or IBLOCK data in the WSIEG1 model (WSIEG1 CONS J+20 to J+33)? These parameters do not exist in IEEEG1 and the values you have used here may be the cause of the difference you are seeing between the 2 models.

Please indicate the WSIEG1 and IEEEG1 model parameters you used. Also please indicate the machine initial conditions (ETERM, EFD, POWER, VARS, PF, ANGLE, ID, IQ) you got when using both IEEEG1 and WSIEG1 models. These will be helpful for finding the cause of your issue.

link

Comments

I enter the random value I wanted for deadband. but another data didn't enter there for NGV, IBLOCK. How can I solve them?

petite cho gravatar imagepetite cho (Jul 6 '17)