Ask Your Question
0

PSSE v33 system MVA base changing

asked 2017-04-17 02:36:33 -0500

IljaM gravatar image

Hi,

How is it possible to change system base MVA in existing PSSE sav case? It seems that there is no python method for that.

BR, Ilja

edit retag flag offensive close merge delete

2 answers

Sort by ยป oldest newest most voted
0

answered 2017-04-21 11:28:52 -0500

Youim gravatar image

You can import your system (.raw) file into powerworld to change the base MVA, and export it back in .raw file for PSSE

edit flag offensive delete link more
0

answered 2017-07-18 19:47:30 -0500

knucklehead gravatar image

You can export your .sav file as .raw, Then edit the first line from 100.00 to your new Base MVA. Keep in mind that all Impedances need to reflect your new Base MVA.

0, 100.00, 33, 0, 1, 60.00  / RAW FILE FIRST LINE

3phasee.com

edit flag offensive delete link more

Comments

Please note it is necessary to recalculate branch R,X,B and line shunts as well as transformer impedance (in system base) to the new base MVA.

perolofl gravatar imageperolofl ( 2017-07-20 15:49:15 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

[hide preview]

Question Tools

1 follower

Stats

Asked: 2017-04-17 02:36:33 -0500

Seen: 2,533 times

Last updated: Jul 18 '17