what is meant by "bus type code and series element status inconsistencies "?

asked Feb 14 '17

vicky gravatar image

hello everyone, i am new to psse ,it will be very helpful if someone clears my doubt.while solving(power flow) a sld with many componets and buses i recieved the following error message "Topology error:3 bus(es) with bus type code and series element status inconsistencies" .In the sld all buses with load alone are intialized as non generator bus,and some buses having either generator alone or both load and generator is initilized as genrator bus and there are two swing bus.

can somebody explain to me why load flow is not executed?

1 answer

Sort by » oldest newest most voted
0

answered Feb 16 '17

perolofl gravatar image

You have most probably in-service brances connected to out of service buses. Use activity TREE to find the details.

link

Comments

Thank you perolofl,

vicky gravatar imagevicky (Feb 16 '17)