Is there an easy way to get a ramping bus voltage in a dynamic simulation?
I have tried varying the fault impedance progressively with each time step, but I dont get an even response.
First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
I have tried varying the fault impedance progressively with each time step, but I dont get an even response.
You need to change the fault impedence each time as per your requirements as get the desired bus voltage.
Eg: I was recently working on a project which needed that the bus voltage drop to 50% during the fault. Changing the impedance from -2e+009 to -1+002 did the trick. It initially took me time to adjust the impedance, but I guess that's the only way round, to be patient!!!!
Asked: 2016-11-01 07:13:48 -0600
Seen: 703 times
Last updated: Nov 05 '16