Blown up power flow solution right after adding short circuit data at the swing generator

I am connecting an infinite generator at a bus (swing bus) and then a branch with R and X values obtained from the short circuit data connects this bus to my system. This is to consider the contribution of the utility side during the dynamic simulation. But I am stuck with a blown up power flow before even considering the system dynamics. I haven't been able to narrow down the problem. I am sure the system is set up right as I was able to run the power flow before adding that R and X branch i.e., the infinite generator with no short circuit data.

Any help in this regard would be very helpful and appreciated.

SKT's avatar
1
SKT
asked 2016-01-28 12:20:33 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

3 Answers

0

Since the load flow was blown up after adding the new generator bus and a branch you should solve again with FLAT START!

perolofl's avatar
3.8k
perolofl
answered 2016-09-19 15:39:25 -0500
edit flag offensive 0 remove flag delete link

Comments

add a comment see more comments
0

Perhaps the R and X values are big changes from PSSE solution point of view. Try modelling the branch with high R and X values and then reduce these gradually in small steps till you reach the desired values.

bad_hand's avatar
1
bad_hand
answered 2016-02-04 22:50:06 -0500
edit flag offensive 0 remove flag delete link

Comments

add a comment see more comments
0

I don't think it work when you applied short-circuit impedance in to reach LF solution. I recommend you change the transient parameter of generator to do dynamic simulation instead of putting a abnormal value of impedance into system.

Cao Huy's avatar
173
Cao Huy
answered 2016-08-08 06:45:20 -0500
edit flag offensive 0 remove flag delete link

Comments

add a comment see more comments