INITIAL CONDITIONS SUSPECT
As I can solve the following?
CONTROL WT4E2 AT BUS 3223 MACHINE CT WRONG INITILIZATION: Eqcmd' 0.3126 EXCEEDS MAXIMUM 0.3093
add a comment
First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
As I can solve the following?
CONTROL WT4E2 AT BUS 3223 MACHINE CT WRONG INITILIZATION: Eqcmd' 0.3126 EXCEEDS MAXIMUM 0.3093
The maximum setting in the model WT4E2 is exceeding the maximum IQmax (Max active current) variable (J+29) in the dynamic model. Try to rise it above 0.3093 or try to raise to Qmx (max limit of voltage regulator) in the dynamic model instead