which phase is considered fault phase during asymmetrical fault in PSSE?

asked 2015-05-28 02:56:18 -0500

sssm gravatar image

we are analysing asymmetrical fault on PSSE, so we need to know during single line to ground fault and line to line fault which phases are considered faulty?

edit retag flag offensive close merge delete

1 answer

Sort by ยป oldest newest most voted
0

answered 2015-06-04 07:34:21 -0500

de_fr gravatar image

For the time domain dynamic analysis, psse can only simulate the symmetrical fault. In the short circuit analyses, we'll get only the short circuit currents of different faults. i.e. single Phase earth failure: the results are same if we have phase a, b or c failure.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

[hide preview]