Zero sequence impedance
asked 2015-03-29 19:31:25 -0600
Anonymous
When i want to apply branch unbalance, but it says invalid BRANCH HAS NO ZERO SEQUENCE IMPEDANCE. It's a 9bus system btw.
Can anyone guide me? Thanks
First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
asked 2015-03-29 19:31:25 -0600
Anonymous
When i want to apply branch unbalance, but it says invalid BRANCH HAS NO ZERO SEQUENCE IMPEDANCE. It's a 9bus system btw.
Can anyone guide me? Thanks
You need to add zero sequence data to your branches. If you go into your "Network Data" and select the "Branch" tab, then scroll right until you see the columns starting with "Zero Seq" you will most likely see that they are blank. This is a problem. What you're trying to do is equivalent to performing a power flow without resistance data.
I manage to perform my power flow simulation as well as dynamic simulation. Just that when i want to apply unbalanced branch fault, this problem occurs: Branch has NO ZERO SEQUENCE IMPEDANCE. When i entered the zero sequence data, and i run again, it shows 'NO PATH TO GROUND'. still figuring out why