Ask Your Question
0

pv analysis question

asked 2013-10-24 05:43:00 -0500

igo87 gravatar image

Hello guys, I have a question about pv analysis in pss/e

I want to set HVDC line as interface between two area (source & sink) in pv analysis

Although i make the monitoring statement as for specifying a two-winding or non-transformer branch data

like seen below

|BRANCH| FROM BUS bsid TO BUS bsid [|CIRCUIT| ckid] |LINE | |CKT |

but above statement does not work for HVDC line for setting monitoring inferface record for monitoring file (*.mon)

Please help me~

edit retag flag offensive close merge delete

1 answer

Sort by ยป oldest newest most voted
0

answered 2013-10-24 18:42:11 -0500

yfwing gravatar image

The 2-Terminal HVDC line has the PSS/E internal assigned circuit id. It could be either '2DI' or '2DR'. It is not recommend to use |BRANCH| FROM BUS bsid TO BUS bsid [|CIRCUIT| ckid] |LINE | |CKT | to include HVDC lines. Suggest use *[MONITOR] BRANCHES|LINES bsid bsid [ckid] END *, you can ignore the [ckid] part.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

[hide preview]

Question Tools

Stats

Asked: 2013-10-24 05:43:00 -0500

Seen: 338 times

Last updated: Oct 24 '13