"MVA/Current expressed as MVA"

asked 2025-09-04 00:01:54 -0500

Yoyo gravatar image

Hello everyone

Can someone please explain to me the meaning in diagram》properties the concepts of "MVA/Current expressed as MVA"? What is the difference between these definitions and when is it correct to define each of them for "Transformer/Non transformer branches?"

I would love an example of the differences.

Thanks!

edit retag flag offensive close merge delete

2 answers

Sort by » oldest newest most voted
0

answered 2025-09-08 08:26:02 -0500

likethevegetable gravatar image

T-Lines are often given an MVA rating because it's easier to relate to the bulk transfer of power and is invariant between nominal voltage levels. But thermal limits of T-Lines are based on current because that's what heats up the metal. So if you express % rating of line based on an MVA flow, the actual current will differ depending on the voltage. Using "Current as MVA" will account for this and give you want, generally speaking.

edit flag offensive delete link more

Comments

Good explanation. Thank you very much!

Yoyo gravatar imageYoyo ( 2025-09-08 10:07:21 -0500 )edit
1

answered 2025-09-14 09:38:16 -0500

perolofl gravatar image

Example: Branch 154 - 205 in savnw.sav network.

Rate A: 600 MVA, flow -354.2 MW -j251.5 Mvar = 434.4 MVA.

When "Non transformer percent units" in Program Setting is chosen to "MVA", the percent loading is 434.4/600 = 72.4%.

The voltage at bus 154 is 0.9389 pu.

When "Non transformer percent units" in "Program Settings" is chosen to "Current expressed as MVA", the percent loading is 434.4/600/0.9389 = 77.1%.

The selection in "Program Settings" determines the unit for loading percentage (MVA or current) used in Reports like POUT etc.

Slider diagrams have their own setting of the option in "Diagram Properties - Diagram annotation". However, there is a severe bug in Slider diagrams. The wrong option is shown in the diagram:

With MVA option:

image description

Here the current loading (77.1%) is displayed instead of MVA loading!

With Current option:

image description

Here the MVA loading (72.4%) is displayed instead of current loading.

The conclusion is to choose the wrong (opposite) option in "Diagram Properties" to get the correct loading information in Slider diagrams.

The bug has been reported to Siemens PTI and will be corrected in the next release.

It is the same bug for transformer.

edit flag offensive delete link more

Comments

Excellent explanation! Thanks for the clarification. From what I understand, there are versions with this bug and there are those without it, it is necessary to check individually for each version.

Yoyo gravatar imageYoyo ( 2025-09-14 09:47:37 -0500 )edit