THR, current threshold (pu sbase)

asked Nov 11 '4

anonymous user

Anonymous

This is the CONS model of TIOCR1 line relay, can anyone show the exact calculation for this threshold value? And what is the difference between THR, current threshold (pu sbase) and lowest operating current (multiple of pickup.)

1 answer

Sort by ยป oldest newest most voted
0

answered Nov 11 '4

perolofl gravatar image

See Program Application Guide, Volume II, Chapter Model TIOCR1.

THR is given in pu current. Inverse time current points (five points) are given in pu of THR, i.e. current values shall be increasing and > 1. Corresponding time values shall be decreasing.

link

Comments

I have already seen the chapter but could not find the exact calculation. In my .dyr file the current threshold is given as 6.7. I am just curious how this value is being calculated?

Current base, Ibase, is Sbase/Vbase/sqrt(3) kA. Ipu = IkA/Ibase. With 100 MVA base and 230 kV the current base is 0.251 kA. 2.5 kA = 2.5/0.251 = 9.96 pu.

perolofl gravatar imageperolofl (Nov 13 '4)

Thank you, much appreciated.