Model FRQDCAT Model Instance 1: Generator bus is not a TYPE 2 bus -- MODEL IGNORED
Do I need to add user written model for this message ?
add a comment
First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
Do I need to add user written model for this message ?
This is a miscellaneous model that trips the generator bus at over- or underfrequency.
In this case there is no generator bus stated in ICON(M+1), so the model is just ignored.
You can ignore this message or remove the model.
The quality of your recieved dynamic data is not good.
Yes, I know there are a lot of errors in the data that I have to troubleshoot.