No active table model for Switched Shunt "1 " at bus " xxx [xxx xxx.00]" -- check this before continuing with the simulation

asked Sep 25 '4

junaid2657@gmail.com gravatar image

What does this error mean? This message appears when I am initializing the dynamic simulation.

1 answer

Sort by » oldest newest most voted
0

answered Sep 25 '4

perolofl gravatar image

There is a switched shunt with continous control but no dynamic model. This is a warning only and can be ignored if the switched shunt shall be kept constant during the dynamic simulation.