TWO-TERM DC LINE "LINE 1" USER MODEL "TXJUD" NOT ACCESSIBLE

asked Sep 19 '4

junaid2657@gmail.com gravatar image

How to access this user model, please can anybody help me out?

1 answer

Sort by » oldest newest most voted
0

answered Sep 19 '4

perolofl gravatar image

You are using an user written HVDC model with name ZXJUD there Z is any letter except "T". These models have a second entry point with the first character repalced with the letter "T". In this case TXJUD. That subroutine is called in "CONET", i.e. at every iteration done by TYSL.

You need to access the dll file with the user model and add it to PSSE before initialising.

link

Comments

Thank you so much for the clarifications. Maybe this is the reason I am not getting Initial condition Check OK message.