Ask Your Question
0

Changing winding ratio of a 3 winding xmf?

asked 2023-08-02 00:38:35 -0500

payamt gravatar image

I'm trying to build a script to lock a certain PF (0.95 leading or lagging) at the POI. My question is whether it's possible to literately adjust the winding ratio (pu) for 3 winding transformers? Would the THREEWNDWINDINGDATA3 python syntax be appropriate for this?

edit retag flag offensive close merge delete

1 answer

Sort by ยป oldest newest most voted
0

answered 2023-08-02 16:09:53 -0500

perolofl gravatar image

Yes, you can use hreewndwindingdata3. For example, to change ratio for winding 1 to 1.01667:

psspy.three_wnd_winding_data_3(ibus2, jbus, kbus, ickt,1, realari1= 1.01667)

The fifth argument is the winding number; 1, 2 or 3.

The unit for the ratio is determined by code CW. It may be in per unit on bus base voltage, winding voltage in kV or per unit on winding nominal voltage.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

[hide preview]

Question Tools

Stats

Asked: 2023-08-02 00:38:35 -0500

Seen: 124 times

Last updated: Aug 02 '23