Model NRCGP3U
may be used to supervise and trip generators in an area, zone etc.
Check the DYRE-file for any call of 'NRCGP3U'.
Check also spreadsheet Dynamics Data - Protection Models - Machine for any tripping models.
2 | No.2 Revision |
Model NRCGP3U
may be used to supervise and trip generators in an area, zone etc.
Check the DYRE-file for any call of 'NRCGP3U'.
Check also spreadsheet Dynamics Data - Protection Models - Machine for any tripping models.
Edit:
Check if option "Scan generators exceeding speed deviation threshold" is enabled in Dynamic Simulation Options:
However, the progress window trip message looks like this so it is not causing your trip:
Machine 1 at bus 3018: PU speed Deviation= 0.05057; PU overspeed Threshold= 0.05000
MACHINE 1 AT BUS 3018 [CATDOG_G 13.800] TRIPPED AT TIME = 1.4300
3 | No.3 Revision |
Model NRCGP3U
may be used to supervise and trip generators in an area, zone etc.
Check the DYRE-file for any call of 'NRCGP3U'.
Check also spreadsheet Dynamics Data - Protection Models - Machine for any tripping models.
Edit:
Check if option "Scan generators exceeding speed deviation threshold" is enabled in Dynamic Simulation Options:
However, the progress window trip message looks like this so it is not causing your trip:
Machine 1 at bus 3018: PU speed Deviation= 0.05057; PU overspeed Threshold= 0.05000
0.10000
MACHINE 1 AT BUS 3018 [CATDOG_G 13.800] TRIPPED AT TIME = 1.4300